Forum » Power Supply » Can we also use hard cable for battery termination in UPS?
Topics: Can we also use hard cable for battery termination in UPS? on Power Supply
#1
Start by
Wajid Ali Chattha
10-20-2013 10:44 PM

Can we also use hard cable for battery termination in UPS?

Is it necessary to use only flexible cable for battery termination in a UPS or can we also use hard cable for the same purpose.
10-21-2013 01:10 AM
Top #2
Hammad Rafiq
10-21-2013 01:10 AM
It is easy to terminate as compared to hard cables.
10-21-2013 03:45 AM
Top #3
Saeed Asghari
10-21-2013 03:45 AM
Flexible cable is good for movable equipments like lifts, robots and etc.
10-21-2013 06:21 AM
Top #4
Alan Maltz
10-21-2013 06:21 AM
It's only necessary if you want ease of installation/termination, ease of individual cell/battery removal, freedom from fear of cracked post seals/battery cases due to mechanical stress/thermal expansion, basically all the advantages of using flexible cable. The main downside is if your termination practices are poor you may experience rapid corrosion between the fine strands and the connector.