Electric Automation Forum
Forum » General Discussion » How to check transformer Oil IR value
Topics: How to check transformer Oil IR value on General Discussion
#1
Start by
Rakesh Prajapati
01-15-2014 09:46 PM

How to check transformer Oil IR value

How to check transformer Oil IR value and what are the test require for transformer oil.
01-16-2014 12:06 AM
Top #2
Paul Hinchcliffe
01-16-2014 12:06 AM
Independent lab?
01-16-2014 02:08 AM
Top #3
Ajikumar Nair
01-16-2014 02:08 AM
Using a meg gar of required voltage level, check the IR and PI Values. Then check the BDV, Tan delta etc on test sample taken appropriately using the test kit. Then you can go for a DGA analysis also in an accredited lab for RLA study.
01-16-2014 04:43 AM
Top #4
Mohammed Azzam
01-16-2014 04:43 AM
Take an oil sample from the transformer drain knope and test it in automatic oil test machine. It consists of two electrods. you put the sample in it and the voltage will start increasing kV/s. Until a spark occure. You repeat the test six times then you take the average. The kV level is your oil break down voltage
01-16-2014 07:16 AM
Top #5
HarisH Shimpi
01-16-2014 07:16 AM
BDV and DGA is testing of Oil. Transformer test as per IS 2026.
01-16-2014 09:43 AM
Top #6
Nabil Metwally
01-16-2014 09:43 AM
Dear Rakish
there are a lot of periodical tests for the oil transformer, you should be carried out every 3, 6 months and every 3 years, 1) oil dielectric strength break down voltage test (every 3 months) if you have a tester. 2) DGA Dissolved Gases Analysis -Total Acid Content-Water content- .
Traces of Furanic compounds to be check if there is (no) significant damage of the cellulosic insulation - Passivator (copper corrosive) content if it is active or not. all previous tests can you send for the lab at least every 6 months. 3) Tan delta every 3 years.
if you need hard copy from these tests , you can send your Email at : nabil.metwaly@powertek-eg.com to forward to you some of these tests
01-16-2014 12:15 PM
Top #7
Siva Kumaar
01-16-2014 12:15 PM
Thanks Mr.Nabil for the useful tips
Regards
01-16-2014 02:48 PM
Top #8
Kishore kumar
01-16-2014 02:48 PM
What is tan delta test and is it possible to carry out check the no load and full load loss of 11/433 stepvdown transformer at site
01-16-2014 05:32 PM
Top #9
Kishore kumar
01-16-2014 05:32 PM
What is tan delta test and is it possible to carry out check the no load and full load loss of 11/433 stepdown transformer at site
Reply to Thread