Rotor Earth fault Tripping
After searching details in DCS trend we found following sequence of events:
1. Control Valve fluctuation
2. Resulted in Load fluctuation due to variation in valve position
3. To overcome above situation AVR excitation changes frequently,
4. Frequent sudden changes resulted in drop in Resistance across Field winding.
5. This has caused the Rotor Earth Fault alarm (Two Times) and consequently tripping of the Turbine.
The present value of Rotor Earth Fault Relay is here under
Alarm - 20 Kohm for 5 Sec, and
tripping - 5 Kohm for 5 Sec.
Based on above phenomenon we have conclusion on frequent change in Excitation system followed by load/CV fluctuation, which have finally converted in Rotor Earth Fault.
for your review & comment