Currents in Y Phase connected to motor.

I was told currents in Y phase will be more when compared with R & B Phases. can anyone explain theory behind this?

Problem: Running load of motor 252A, cable length: 200mtrs.
09-01-2014 06:12 PM
Top #2
Alan Maltz
09-01-2014 06:12 PM
Satish,

What are the currents?

Alan
09-01-2014 08:29 PM
Top #3
satish nurukurthi
09-01-2014 08:29 PM
what should be current in Y phase if R and B phase currents are 252 A?
09-01-2014 11:14 PM
Top #4
Norman Chambers
09-01-2014 11:14 PM
The same, what is the current reading of Y phase? we cannot asses the situation without this value.
09-02-2014 01:54 AM
Top #5
satish nurukurthi
09-02-2014 01:54 AM
Mr. Norman: Value is 257A
09-02-2014 04:01 AM
Top #6
John Bird
09-02-2014 04:01 AM
A three phase motor can be connected with the windings in star or in delta connection. Star and delta are often abbreviated as Y and D. Is it that somebody has told you that a motor connected in Y will have higher current? Possibly they used the letter "Y" when talking about star connection rather than referring to Yellow phase.

A different possibility - are the controls and contactor coils for this motor connected to Y phase, hence you will measure slightly higher current in the yellow supply lead?
09-02-2014 06:22 AM
Top #7
Norman Chambers
09-02-2014 06:22 AM
This could be a supply transformer issue. The voltage difference falls within 3% of the voltage nominal and is normal.

I see nothing the value which you should be worried about. You can have your supplier do a tap change to satisfy you.

Kind Regards
09-02-2014 09:10 AM
Top #8
Ing. Ole Knudsen
09-02-2014 09:10 AM
Such a small difference between phase currents can be caused by a variety of factors.

One of the most likely causes could be that the supply is via three single-core cables, that are not laid absolutely symmetrically, and with no regular transpositions along the way.

Another cause could be measuring error, in particular if it is difficult to place some clamp-on tong tester so the readings will not be affected by stray magnetic fields from the other two cores.

Such a small difference will rarely be something to be concerned about.